Actually you can also roughly change minutes remaining by using APC powerchute app,by changing the value under the number of batteries connected.Six months is the expected battery life if you partially discharge it everyday. Bigger batteries may last a year. The UPS is much stricter about the minimum voltage than cheap inverters.
I started with 2x 150 AH Okaya Big Yellow which died after six years. I replaced them with 2x 150 AH Okaya TT 5024 two years ago.
The UPS requires a manual calibration for unsupported batteries like this. Charge them fully for 48 hours, run a constant 30% load (do not change the load) and let the UPS run until it switches off. Disable the auto-shutdown or unplug the USB cable. Until I did this it randomly malfunctioned as if the batteries were dead. It showed errors like No Battery, 0 minutes remaining, etc.
The UXI has the same firmware of the SUA1000XLI which is sold elsewhere except india and it gets a 18AH C20 battery ,yes sealed lead acid batteries have a high voltage sag under load and their capacity takes a hit mostly after first or third complete discharge,compared to flooded tubular batteries which are designed for deep discharge.According to the calculation I did a long time ago, the correct number for 2x 150 AH C10 was 4 packs since the stock batteries were 12 V 7 AH each. It did not help in the end as the runtime remaining was value completely unreliable.
The only models that properly support charging and reporting of flooded lead-acid batteries are the SRC2KUXI, SRC3KUXI etc. These are designed to be used as an inverter and have live, neutral & ground outputs at the back for wiring.