That is a lot of conversion losses there, AC -> DC (Inverter battery) -> AC (UPS) -> DC (UPS battery) -> AC (PC) -> DC (onboard components).
@rahuljawale I don't think that's true when AC power is present. The inverter/UPS will bypass the battery and supply AC directly to the connected appliance.
As for when there's no power, again inverter will supply from battery to UPS, UPS will bypass its own battery and supply to PC because in view of UPS the power is present.
While battery charging it's what it is... since it's converting energy it is understood some will be lost as heat.
I agree with other points for sure but the thing is power outage is not my main concern here as they are minimal to none. The problem here is since past 2-3 months we're getting a lot of voltage surges and power fluctuations.
When my PC was on load and any of the above happens it just trips my inverter into overload state probably due to less capacity (900VA), PC power usage is 400-450W (approx.) from wall. It's fine when idle or CPU load is there but it can't handle GPU load. I also tried just the PC on inverter and nothing else, but nope...
Anyways, I did think of increasing inverter capacity but the investment amount is really high (at least 30-35K or more for inverter + 2x batteries) and there was no guarantee of switching time being optimal. Dealers here won't take it back if it doesn't serve my purpose.
As I don't need the backup for anything more than 5-10 mins the UPS way is cost effective to me and pretty much guaranteed optimal switching time.
Hence I did buy the APC BX1100C a couple days ago and the problem is solved. I will not keep it plugged to the inverter but to the mains directly. If power cut happens and it's is a bit longer (which happens very rarely, I can't even recall the last time it happened), I will switch the input from mains to inverter for the UPS after I reduce or remove the load on the PC.
To others,
To be tested:
Backup time on normal load and full load.
Connecting inverter output to UPS input and simulating power cut while PC on full load. I need to check does it trip the inverter or not.
Got a chance today...
Backup on normal load is around 30 mins and on full stress load is 2-3 mins.
The inverter still trips and goes down. I will keep the UPS plugged into the mains, if power goes out for longer than expected (very rare) I will have to manually switch the UPS input power from mains to inverter after reducing load on PC or putting it to sleep mode.