asheet said:
Hi
Pl understand how the Stablilizer rating is calculated.
VA is not same as wattage. VA is just a multiple of Voltage x current.
Wattage is Voltage x current x power factor. For all inductive loads, the power factor is less than 1. So actual Wattage will be less but VA will be more.
Method of selecting stabilizer :-
1. Chk the Voltage & current rating of the device. It will be written on the sticker near power socket else check teh manual.
2. Voltage will be 220V always.
3. So multiply 220 x Current of all devices and then add the individual devices VAs. Suppose your final figure after adding all VAs is 500, add 25% safety margin to arrive at Stabilizer rating. If u r planning to add more devices later, keep buffer for them.
Hope this helps.
In case ur Stabilizer has a rating in watts also, assume a Power factor of 0.8.
hi asheet!!thanks for a very detailed reply.my samsung TV has
115 watt power mentioned on its back cover sticker.so lets do the calculation, please correct me if iam wrong. as per the formula, 1) wattage=voltage X current X powerfactor
2)VA=voltage X current
lets assume power factor of 0.8 for TV as well as the set top box.
calculating total VA for TV:
wattage=voltage X current X powerfactor
115=220 Xcurrent X 0.8
115
current = ------------ =0.653 amps 0r roughly 0.7 amps
220 X0.8
VA = voltage X current
VA = 220 X 0.7
VA =154
now considering safety margin of 25% , 154 X 1.25=192.5 VA or roughly 200 VA is required for TV alone.
calculating total VA for SET TOP BOX:
wattage=voltage X current X powerfactor
25=220 Xcurrent X 0.8
25
current = ------------ =0.142 amps 0r roughly 0.15 amps
220 X0.8
VA = voltage X current
VA = 220 X 0.15
VA = 33. considering safty margin of 25 % , 33 X 1.25 =41.25 or roughly 50 VA.
so total VA = 200(TV) + 50 (STB) =250 VA Required.
also considering what janitha mentioned about "surge current" i guess 300 VA is what i should be looking for.hope i have got the calculations right. i am looking for V-guard stabilizer,is there any other good brand ?