As new users start to buy Inverter ACs, there's a lot of hue and cry when people aren't able to replicate certain user's bills. Rather than have these people dilute the discussion in all the Inverter threads because they are referencing advertising material, let's help explain what is actually happening.
1. Sharp's Inverter AC Power Saver Calculator is rubbish. Do not use it. Period.
Mistakes :
#Duty cycle of the non-inverter AC is calculated at 100%. Duty cycle = how long the compressor stays ON.
If you notice, the non-inverter's hourly power usage is :- 446 units / 31 days / 8 hours = 1.8KW. The non-inverter's peak power consumption is also 1.8KW. In other words the AC is running at a 100% duty cycle i.e. compressor is always ON, which does not happen under normal circumstances.
If it does happen to run at a consistent 100% duty cycle, then the heatload is a consistent ~5.2KW (1.8KW x 2.9 COP for 2 star = ~5.2KW). If the Inverter AC needs to cool a heatload of 5.2KW, it will consume 1.44KW as per specs, not 875W.
# An additional minor mistake as pointed out by members below is the different tariff slabs which should not apply
1. Sharp's Inverter AC Power Saver Calculator is rubbish. Do not use it. Period.
Mistakes :
#Duty cycle of the non-inverter AC is calculated at 100%. Duty cycle = how long the compressor stays ON.
If you notice, the non-inverter's hourly power usage is :- 446 units / 31 days / 8 hours = 1.8KW. The non-inverter's peak power consumption is also 1.8KW. In other words the AC is running at a 100% duty cycle i.e. compressor is always ON, which does not happen under normal circumstances.
If it does happen to run at a consistent 100% duty cycle, then the heatload is a consistent ~5.2KW (1.8KW x 2.9 COP for 2 star = ~5.2KW). If the Inverter AC needs to cool a heatload of 5.2KW, it will consume 1.44KW as per specs, not 875W.
# An additional minor mistake as pointed out by members below is the different tariff slabs which should not apply