Bought an EV about 10 days ago (MG Windsor Pro)
My society here in Thane has a big MLCP building where all cars are parked (8000+ capacity)
Home charger supplied by MG is 7.2KW
Below is what i have completed in terms of pre-requisite before the MG motors appointed vendor can come & install the charger:
1. MSEB EV meter has been applied & approved - should be installed this week in the MLCP building's Meter room
2. Load approved is 7.5KW - SIngle phase (confirmed with MG charger installation vendor that Single phase is ok)
Below is pending:
1. Cabling from Ground floor of MLCP to 3rd floor parking - Distance is 125 meters
Help needed:
- Need to decide if using an Aluminium cable instead of copper for the majority distance from Ground floor meter room to Parking slot ( ~125 meters) can be done using 10 sq.mm or 16 sq.mm Aluminium 3 core Armoured cable?
- Do a circuit breaker based switchover from Aluminium to Copper cable for last few meters up until the MG 7.2 KW charging unit.
- Does usage of Aluminium cable for majority of the distance result in comparitively higher power loss & subsequently more unit consumption recorded in the MSEB meter?
Any inputs or experience from fellow EV owners will be greatly appreciated, thanks.
P.S: We have about 16 Tata Power EZ charge community chargers installed in the ground floor of MLCP. Below are the issues:
1. About 8 to 9 of them are always not working.
2. Even with the working ones there is frequent disconnection that i have faced & then i need to restart the charging process from Tata power app.
3. Cost per unit is about 14.5 INR + GST as compared to your own MSEB EV meter that comes at a subsidized rate of 7 to 7.5 INR per unit.
My society here in Thane has a big MLCP building where all cars are parked (8000+ capacity)
Home charger supplied by MG is 7.2KW
- They include 10Mtr copper 10 sqm mm Armoured 3 core cable.
Below is what i have completed in terms of pre-requisite before the MG motors appointed vendor can come & install the charger:
1. MSEB EV meter has been applied & approved - should be installed this week in the MLCP building's Meter room
2. Load approved is 7.5KW - SIngle phase (confirmed with MG charger installation vendor that Single phase is ok)
Below is pending:
1. Cabling from Ground floor of MLCP to 3rd floor parking - Distance is 125 meters
- I am yet to purchase the cable & get the cabling done via local electrician
Option 1: Copper Armoured 3 core 10 Sqmm cable: Polycab ~ 380/- per meter (48k/- INR)
Option 2: Aluminium Armoured 3 core 10 Sqmm cable: Polycab ~ 105/- per meter (13k/- INR)
2. EV charger installation by MGHelp needed:
- Need to decide if using an Aluminium cable instead of copper for the majority distance from Ground floor meter room to Parking slot ( ~125 meters) can be done using 10 sq.mm or 16 sq.mm Aluminium 3 core Armoured cable?
- Do a circuit breaker based switchover from Aluminium to Copper cable for last few meters up until the MG 7.2 KW charging unit.
- Does usage of Aluminium cable for majority of the distance result in comparitively higher power loss & subsequently more unit consumption recorded in the MSEB meter?
Any inputs or experience from fellow EV owners will be greatly appreciated, thanks.
P.S: We have about 16 Tata Power EZ charge community chargers installed in the ground floor of MLCP. Below are the issues:
1. About 8 to 9 of them are always not working.
2. Even with the working ones there is frequent disconnection that i have faced & then i need to restart the charging process from Tata power app.
3. Cost per unit is about 14.5 INR + GST as compared to your own MSEB EV meter that comes at a subsidized rate of 7 to 7.5 INR per unit.